Wency Pan
更新时间 2022-07-27 04:46:36 UTC

Hi Juan,


The "E2" code indicates that you might have an open circuit. Could you please check if the valve is connected or broken? 

You might also want to check whether there are shorted zones or open zones. You just need to use a multimeter to measure the resistance between the common wire and each zone (remove the wires from the slots before testing the resistance). The normal reading would be 20-60 Ohms. If the reading is less than 10 Ohms then you might have a shorted circuit in the solenoid and if it is larger than 80 Ohms you might have an open circuit. 


Thanks, 
Wency 
Netro Support

浏览: 1478    点赞: 0


Juan Brea
2022-07-27 09:52:32 UTC  
Hola Wency,
La resistencia me da 48 ohmios, si mido los voltios en la salida del Spark entre el común y la zona que falla me da 0 voltios, antes he retirado los cables (común y zona) y he medido directamente la salida.
Voy a probar a poner una electroválvula directa a la salida, sin usar el cableado del terreno y os comento el resultado.
Saludos

Juan Brea
2022-07-27 10:34:15 UTC  
Wency
He hecho varias cosas:
He puesto una electroválvula nueva directamente a la salida común y a la zona que falla, la he activado manualmente desde la app y sigue sin darme voltios.

He cambiado el cable de la zona 4 a la salida 5 y el cable de la zona 5 a la salida 4, las he activado manualmente desde la app y FUNCIONAN LAS DOS ZONAS. He vuelto a poner los cables en las salidas correctas y siguen funcionando las dos zonas ????.

Ahora la zona 7 ha dejado de regar y aparece E1 en el SPARK 😭😭

Saludos

Juan Brea
2022-07-28 08:39:19 UTC  
Ya está solucionado en la zona 7 tenía un problema de cableado, que el programador anterior (Toro) no detectaba.
Gracias por la ayuda.
Wency Pan
2022-07-29 01:47:40 UTC  
Hi Juan,

Glad to hear it works and please let us know if you have any further questions.

Thanks,
Wency