Zone not watering keep loading

Fabio Pellizzoni
Actualizado 2021-04-13 20:10:43 UTC
Tema: Netro App

Hi

It happened recently that the app shown "online" and  i tried to start one zone  but didn t  work. the count down start but the message loading keep showing and the zone never actually start

Do you have any idea why ?

Thanks 

Ver: 4050    Seguir: 1   

1 Respuesta    Haga clic en la respuesta para ver la respuesta completa y los comentarios.


Netro Inc
Actualizado 2021-04-14 01:27:32 UTC

Hi Fabio,


Please check the wires. Are they loose or disconnected from the slots? Please also check the common wires and the master valve if you have one. If you believe the wires are correctly installed,  please check if there is a main valve/faucet that is turned off manually. 


To test if the controller is working properly, use a multimeter (AC voltage mode) to test the voltage between the common wire and the zone wire when the zone is active. Normally the voltage should be between 24V and 28V.

You might also want to check whether there are shorted zones or open zones. You just need to use a multimeter to measure the resistance between the common wire and each zone (remove the wires from the slots before testing the resistance). The normal reading would be 20-60 Ohms. If the reading is less than 10 Ohms then you might have a shorted circuit in the solenoid and if it is larger than 80 Ohms you might have an open circuit. 


Please let us know if it works. If it still fails, please send us email to support@netrohome.com with your Netro account registered email.


Thanks,

Netro Support